As a developer, you need to know the ID number of thermostat firstly. 

For example, the ID number is 4664.
1. As the ID is encrypted, you need to calculate the effect ID_Effect. 
ID_Effect=(ID+1)*65535+65535=12 39 ED C6 (4 bytes).
2. When you know the number of ID_Effect, you need to communicate with the server of domain name bestbeca.cn.
The engineer should use the server of domain name to analyse the real ip address. The port is 25565.
The developer need to send 12 39 ED C6 for the registration then use the tcp protocol for communication . 
3. After that,  all the parameters of thermostat will be controlled according to the 8 byte datas in the following protocol detail .
4. When thermostat sends collected temperature data to upper computer,  the value of collected temperature should be multiplied by 2 and sent completely by the format of HEX because the accuracy is 0.5.
For example:  When the collected temperature is 25.5,  the value sent by thermostat to the upper computer will be 33H (the demical is 51 ); 
Similarly, When upper computer sends set temperature data to thermostat,  the value of set temperature should be multiplied by 2 and sent completely by the format of HEX because the accuracy is 0.5.
For example:  When the set temperature is 25.5,  the value sent by upper computer to the thermostat should be 33H (the demical is 51).
E.G.: Read Temper= 25.5C
The send(or receive) value is 25.5*2=51
The data in HEX =33H

Communication Protocol And DataFormat Describe

Declare:  Following " 0X " Mean's HEX Values

;;=======================================================================================================================

      1Data Package protocol as below:

      		COMMAND + ID0 + ID1 + Data0 + Data1 + Data2 + Data3 + CheckSum

         8 Bytes in total

;;=======================================================================================================================

      2: CheckSum definition:     

	  (size: 8 Bits)
          CheckSum = (COMMAND + ID0 + ID1 + Data0 + Data1 + Data2 + Data3) & 0xFF ^ 0xA5

;;========================================================================================================================

      3: COMMAND definition
            
            ReadPC read data from thermostat
            WritePC transmit data to thermostat 

            COMMAND is command opcodesize: 8 Bit commands as below
                  command
                PC ------->thermostat
                  [0XA0] --> PC read all data from thermostat
                  [0XA1] --> PC transmit all data to thermostat 
	          [0XA8] --> Time setting
                  
                 
                          command
                  Thermostat--------->PC
		  [0X50] -->thermostat returns all data to PC
		 

;;===============================================================================

      4: ID0 , ID1 definition       
Note:
 	  ID0,ID1  must be 01 01,it is fixed,can not be other data 
    

;;===============================================================================
	  
      5: Data Package definition  
	     
             Data0 ~ Data3 is command operand size is 32 Bit (4 Bytes) 
	     ;;------------------------------
	
             COMMAND1: 0XA0      
	     Data Package0XA0 + ID0 + ID1 + Data0 + Data1 + Data2 + Data3 + CheckSum
	               Data0		00
	               Data1		00
	               Data2		00
	               Data3		00
	     ;;------------------------------
    
	     Response: 0x50  data returns

	  ;;------------------------------    
	  
	  COMMAND2: 0XA1      
	  Data package0XA1 + ID0 + ID1 + Data0 + Data1 + Data2 + Data3 + CheckSum

	               Data0      =>Bit1-Bit0  fan speed
                                 00 -> auto
                                 01 -> high
                                 10 -> medium
                                 11 -> low
                                 
                                 Bit2       must be 0
                            	 Bit3       Manual and weekly programmable
                                          0 -> Weekly programmable
                                          1 -> Manual       
                            
                            	 Bit4       turn-on/off
                                          0 -> turn-off
                                          1 -> turn-on
                            
                            	 Bit6-Bit5       heating and cooling
                                               00->cooling
                                               01->heating
                                               10->ventilation

                               Bit7      A flag for valve open
            
            	   Data1       =>  temperature calibration, -9-9 degree C(0XF7-0X09)
            
            	   Data2       =>  temperature setting, from 10 to 30 degree C (0X0A-0X1E)
            
            	   Data3       =>  ambient temperature
	   ;;------------------------------ 

	   response:  0x50 returns   OK
	   ;;------------------------------      	


	   COMMAND9: 0XA8      
                    Data package0XA8 + ID0 + ID1 + Data0 + Data1 + Data2 + Data3 + CheckSum
		 
		             Data0       =>  second(BCD code)
            
            	   Data1       =>  minute(BCD code)
            
            	   Data2       =>  hour(BCD code)
            
            	   Data3       =>  week(BCD code)
	  ;;------------------------------ 

	  response: 0x50  returns OK
    ;;------------------------------   
      
          
;;===============================================================================
;;===============================================================================
 response: 0x50  OK
 Data package0x50 + ID0 + ID1 + Data0 + Data1 + Data2 + Data3 + CheckSum   	
                  
                  Data0      =>  Bit1-Bit0  fan speed
                                 00 -> auto
                                 01 -> high
                                 10 -> medium
                                 11 -> low
                                 
                                 Bit2       0
                            	   Bit3       Manual and weekly programmable
                                            0 -> Weekly programmable
                                            1 -> Manual       
                            
                            	   Bit4       turn-on/off
                                            0 -> turn-off
                                            1 -> turn-on
                            
                            	   Bit6-Bit5       heating and cooling
                                            00->cooling
                                            01->heating
                                            10->ventilation

                 
                            	   Bit7       A flag for valve open
            
            	    Data1       =>  temperature calibration, -9-9 degree C(0XF7-0X09)
            
            	    Data2       =>  temperature setting, from 10 to 30 degree C (0X0A-0X1E)
            
            	    Data3       =>  ambient temperature
                  
;;===============================================================================
;;===============================================================================
      
      6: Example of 2 commands

          PC is master  thermosat is slave
      ----------------------------------------------------------
      
      ----------------------------------------------------------
      master read data from thermostat
            COMMAND     ==  0XA0       PC read data from thermostat
            ID0,ID1     =>  IP
            Data0       =>  0xxx
            Data1       =>  0xxx
            Data2       =>  0xxx
            Data3       =>  0xxx
            CheckSum
            
     slave respond 
			COMMAND     ==  0X50       thermostat responds data to PC
            
            ID0,ID1     =>  01 01
            
            Data0       =>  Bit1-Bit0  fan speed
                                 00 -> auto 
                                 01 -> high 
                                 10 -> medium 
                                 11 -> low 
                            Bit2       0     
                            Bit3       standby
                            
                            Bit4       turn-on/off
                                  0 -> turn-off
                                  1 -> turn-on 
                            
                            Bit6-Bit5       cooling and heating
                                  00->cooling
                                  01->heating
                                  10->ventilation

                            Bit7       valve 
                                  0->turn-off 
                                  1->turn-on
                            
                            Bit7       standby 
            
            Data1       =>  temperature calibration
            
            Data2       =>  temperature setting from 10 to 30 degree
            
            Data3       =>  ambient temperature
            
            CheckSum
            
      ----------------------------------------------------------
      
      ----------------------------------------------------------
      PC transmit all data to thermostat
            COMMAND     ==  0XA1       PC transmit all data to thermostat
            
            ID0,ID1     =>  01 01
           
            Data0       =>  Bit1-Bit0  fan speed
                                 00 -> auto 
                                 01 -> high 
                                 10 -> medium 
                                 11 -> low 
                            Bit2       0  
                            Bit3       standby 
                            
                            Bit4       turn-on/off
                                  0 -> turn-off
                                  1 -> turn-on 
                            
                            Bit6-Bit5       cooling and heating 
                                  00->cooling
                                  01->heating
                                  10->ventilation

                            Bit7      valve
                                  0->turn-off
                                  1->turn-on
                            

            
            Data1       =>  temperature calibration
            
            Data2       =>  temperature setting from 10 to 30 degree
            
            Data3       =>  standby
            
            CheckSum
            
      slave response
			COMMAND     ==  0X50       PC transmit all data to thermostat   OK
            
            ----------------------------------------------------------